QQ登录

只需一步,快速开始

登录 | 注册 | 找回密码

三维网

 找回密码
 注册

QQ登录

只需一步,快速开始

展开

通知     

全站
5天前
查看: 2895|回复: 2
收起左侧

[已解决] TN-C-S系统中的TN,C,S分别的英文单词是什么?

 关闭 [复制链接]
发表于 2007-7-10 09:16:17 | 显示全部楼层 |阅读模式 来自: 中国北京

马上注册,结识高手,享用更多资源,轻松玩转三维网社区。

您需要 登录 才可以下载或查看,没有帐号?注册

x
TN-C-S系统中的TN,C,S分别的英文单词是什么?不要中文,谢谢!
3 X6 D+ z4 n6 A; @* ^( s' E3 `8 [2 D0 o* _; m' u
[ 本帖最后由 bdblbyq 于 2007-7-11 12:34 编辑 ]
发表于 2007-7-10 18:05:52 | 显示全部楼层 来自: 中国河南南阳

仅供参考

Terra Neutral-Combined-Separate 9 k. I+ |1 H+ V1 c2 s; T+ T

+ Q! \  C" l4 O3 X% k; y  N7 d  _9 i
7 u$ C( X* j6 m8 o3 Z
International standard IEC 60364 distinguishes three families of earthing arrangements, using the two-letter codes TN, TT, and IT.1 D1 O$ ]  s2 u) y  e/ b
( ~3 U4 z2 A/ e: h* U
The first letter indicates the connection between earth and the power-supply equipment (generator or transformer):
3 R/ l& N- |$ ~
  x. Z3 D& w8 B* p1 e8 g3 zT  :  direct connection of a point with earth (French: terre);
) m  d$ Z+ I' t& N4 \& oI  :  no point is connected with earth (isolation), except perhaps via a high impedance.
$ Q9 d- }7 A8 W5 S3 B' j5 D
: y  W- @8 @# z+ P5 TThe second letter indicates the connection between earth and the electrical device being supplied:
2 `* ^4 Z7 @. G% R% x+ n
2 D* [6 w% M0 i+ a3 JT  :  direct connection with earth, independent of any other earth connection in the supply system; 0 X0 d4 z7 S% N/ n
N  :  connection to earth via the supply network
: a9 d9 _3 E# e( Y- m; X  g7 n$ }& @4 T0 e0 j; W  j

& q6 H; `+ Z: m+ ]! EThe conductor that connects the exposed metallic parts of the consumer is called protective earth (PE). The conductor that connects to the star point in a three-phase system, or that carries the return current in a single-phase system, is called neutral (N). Three variants of TN systems are distinguished:
2 N- D1 c$ I* Y6 _# t& Q3 z, {1 a1 M) s
TN‑S  :  PE and N are separate conductors that are connected together only near the power source.
" T& K# t- n$ s4 e, Y; DTN‑C  :  A combined PEN conductor fulfils the functions of both a PE and an N conductor.
+ W# [. K. |2 m( S% X- qTN‑C‑S  :  Part of the system uses a combined PEN conductor, which is at some point split up into separate PE and N lines. The combined PEN conductor typically occurs between the substation and the entry point into the building, whereas within the building separate PE and N conductors are used. In the UK, this system is also known as protective multiple earthing (PME), because of the practice of connecting the combined neutral-and-earth conductor to real earth at many locations, to reduce the risk of broken neutrals - with a similar system in Australia being designated as multiple earthed neutral (MEN).

评分

参与人数 1三维币 +5 收起 理由
bdblbyq + 5 应助

查看全部评分

 楼主| 发表于 2007-7-11 09:21:30 | 显示全部楼层 来自: 中国北京

很详细

很详细,谢谢!有关它的英文标准吗?
发表回复
您需要登录后才可以回帖 登录 | 注册

本版积分规则

Licensed Copyright © 2016-2020 http://www.3dportal.cn/ All Rights Reserved 京 ICP备13008828号

小黑屋|手机版|Archiver|三维网 ( 京ICP备2023026364号-1 )

快速回复 返回顶部 返回列表