TN-C-S系统中的TN,C,S分别的英文单词是什么?不要中文,谢谢!2 v7 x" A* H5 e2 b2 u+ a0 |4 M( |* f

2 q: ]2 S5 R* s$ n1 z* {6 n: d9 K[ 本帖最后由 bdblbyq 于 2007-7-11 12:34 编辑 ]
发表于 2007-7-10 18:05:52 | 显示全部楼层 来自: 中国河南南阳

仅供参考

Terra Neutral-Combined-Separate
/ `4 t( Y# e/ N, R: A
9 `2 o' K: J( i
, m6 E7 R" d' j6 C
* T  ^% g# l7 N- T) IInternational standard IEC 60364 distinguishes three families of earthing arrangements, using the two-letter codes TN, TT, and IT.
6 `+ e0 C: {  |+ v! b* A9 }4 ~- ^# I- f  V0 H
The first letter indicates the connection between earth and the power-supply equipment (generator or transformer):
+ D3 J# p; Y" T8 ~2 G% ?2 s& Y/ j) C" m0 Z
T  :  direct connection of a point with earth (French: terre);
4 S0 m( b3 U# N, i6 C0 RI  :  no point is connected with earth (isolation), except perhaps via a high impedance.
. T% {! Q3 ~; x' D3 M7 ^: \. b9 \7 b# Y# u9 F* m  ?, x! F4 u4 o
The second letter indicates the connection between earth and the electrical device being supplied:2 |; e# b/ Y5 P8 M( f! v; D4 h' X8 \
8 J) P% T, N7 s& s9 e
T  :  direct connection with earth, independent of any other earth connection in the supply system;
$ |$ }( t2 ]$ I1 j# |5 f3 C2 ^8 DN  :  connection to earth via the supply network
/ ]" N, Y# ~& I  P% F8 W0 ^; K
4 s* G2 z, @/ P8 u- A  v1 t' H* r) ]
The conductor that connects the exposed metallic parts of the consumer is called protective earth (PE). The conductor that connects to the star point in a three-phase system, or that carries the return current in a single-phase system, is called neutral (N). Three variants of TN systems are distinguished:
- I( @/ [' a4 Z9 b5 ]1 S$ R* n: m( Q" q; [$ S
TN‑S  :  PE and N are separate conductors that are connected together only near the power source. + D& a9 ^, l+ ?3 F4 L6 Q
TN‑C  :  A combined PEN conductor fulfils the functions of both a PE and an N conductor.
: F, d$ c% K" s. {5 L; \TN‑C‑S  :  Part of the system uses a combined PEN conductor, which is at some point split up into separate PE and N lines. The combined PEN conductor typically occurs between the substation and the entry point into the building, whereas within the building separate PE and N conductors are used. In the UK, this system is also known as protective multiple earthing (PME), because of the practice of connecting the combined neutral-and-earth conductor to real earth at many locations, to reduce the risk of broken neutrals - with a similar system in Australia being designated as multiple earthed neutral (MEN).